PLEASE STOP SELLING THIS DANGEROUS PLUG ADAPTOR
Many sellers are selling a VERY DANGEROUS ELECTRICAL PLUG ADAPTOR/s right here on eBay! 5-7 different models.
I have been unsuccessful in contacting eBay, since they do not respond and seem not to care about the dangers involved with this unsafe plug adaptor.
How can I get eBay to respond? That is my question and goal?
They need to take IMMEDIATE ACTION before someone gets seriously HURT!
STOP SELLING IT & RECALL ALL OF THEM!
----------MORE INFO------------
These plug adaptors imply and show how they convert a standard “e26 lamp socket†into a 3-wire grounded 120Vac receptacle!
NO, They DO NOT! It’s Impossible!
A standard e26 lamp socket has NO ground connection in it, so it is IMPOSSIBLE to convert it into a GROUNDED receptacle.
A standard e26 lamp socket only has 2 connections, Hot & Neutral, it has NO GROUND connection.
Again, these plug adaptors are very DANGEROUS, since you may think you have a 3 wire grounded receptacle, when you DO NOT.
Very misleading, especially when the appliance you are plugging into this adaptor requires the 3-wire ground.
None of these adaptors are UL Listed and will never be, because their DESIGN IS DEFECTIVE. They all have OPEN GROUND connections!
If you want to test this dangerous adaptor yourself, just buy this $10 Klein Circuit tester RT210 (UL Listed) at Home Depot.
https://www.homedepot.com/p/Klein-Tools-Receptacle-Tester-RT110/206517828
Plug it into the adaptor you are selling and see the OPEN GROUND result!
*This circuit Tester is also recommended to test all the 3 wire receptacles in your own home.
Many of these DANGEROUS plug adaptors are being sold online by eBay, Amazon, Walmart, Sears and others!
I have contacted them about the dangers, but they do not respond and continue to sell these DANGEROUS plug adaptors.
Why I just do not know.
So, your help is needed to some how contact eBay and find out why they are doing nothing about it?
Please also spread the word about these DANGEROUS plug adaptors.
Just share this information with your Friends, and hopefully they will share it also.
This information may just save a user from ELECTRIC SHOCK, AND OR ELECTROCUTION!
I am a retired Electrical Engineer and have extensive experience in the power electrical field for many many years. I also worked as an Electrician for many years before and during college.
THIS PLUG ADAPTOR IS NOT SAFE TO USE, and you are putting yourself at risk when the ground connection is required by the item you are plugging into it.
spark-chaser1
To the OP… you would be better served by petitioning the NFPA. Your input won’t make it into the deliberations for the NEC this cycle. But they will be starting to compile submissions for the next.
They do listen. most of the National Electrical Code is founded on submissions such as yours.
varebelrose
The problem is that the NFPA and the NEC have no bearing with these Chinese made items. Tons of stuff is imported into the US constantly with either no or fake listing agency qualifications. The only way to stop them is the same as stopping counterfeit imports... at the border or port, and we know thats not going to happen.
Trivia.. OSHA actually recognizes 21 NRTL associations, the UL is just one of them. I deal with a lot of imported industrial equipment, so have to be on the lookout.
https://www.osha.gov/nationally-recognized-testing-laboratory-program/current-list-of-nrtls
spark-chaser1
I see these used in basements and garages to ‘ make’ outlets out of lights. Also used in outside lights to do the same thing. I’ve even seen cables made onto cord caps and plugged into these to FEED CIRCUITS because the homeowner didn’t want to feed out of the panel.
No grounding, no gfci protection.
This is happening everywhere, every day, in this very world.
These devices have their uses… for people who know the hazards associated with them , only use them temporarily, and take precautions.
there isn’t really a lot of room for debate… these are not being safely used for their intended purposes, and that is why this is such an issue, they will continue to be sold, and people will continue to misuse them. It is up to electrical professionals to warn people of the hazards, and if people choose to ignore it, so be it.
spark-chaser1
It is also correct that the NFPA /NEC won’t do anything about these “ temporarily permanent†disaster dispensers, leaving it to US in the industry to warn people. Hardly a day goes by that I don’t find myself having to save people from themselves and it does get tiring to do so.
annadryl
People are temporarily-permantly using a lamp jack hack cable almost daily where you are? What world is this?
campanaelia
I don't know what type of places your working in, but it sounds like a jungle out there if you have to save people everyday. I can only think of once in 30 years I had to save my partner that got bit by 277v lighting circuit while working on a scaffold.
TBH, I never seen anybody use these plud adapters since I never did residential work except for friends and family. I was in the "A" division of the IBEW and did all commercial work, like shopping malls, Walmarts, Costcos, defense contractors, water treatment and power plants, etc. I was also a lighting specialist for shows, concerts, and sporting events. I did every installation to code and always took classes every 3 years to stay up to date for changes.
I'm certainly not condoning these plug adapters but as @varebelrose stated, the ground is probably tied to the neutral which is a lot safer than "the average John Doe homeowner" using a 2 to 3 prong adapter for a 3 prong cord cap. That is, without a doubt, an open ground, so I certainly wouldn't lose any sleep over it.
spark-chaser1
We are transitioning to all industrial and getting out of residential, because it really is a jungle. In the both states I’m licensed in, homeowners can do their own wiring. A lot of condo owners and apartment landlords misinterpret that and also do their own work, and it’s not pretty. Also, my area has a lot of lakefront, and camp owners do their own wiring after downing a 30 pack. So devices like this are right up their alley as a legit wiring method.
It sounds like I’m exaggerating, unfortunately I’m not.
I’m thankful that these people don’t have access to 600v or 480/277 3 - phase.
campanaelia
These plug adapters are meant for temporary power, and even though they are ungrounded from the light socket base. the third prong can come in handy to plug in GFI protector cord. The GFI adapter will supply the ground protection necessary, even when there is none present. I'm a retired IBEW inside wireman and always used GFI protectors when working outdoors or on jobsites.
https://www.ebay.com/itm/204212604028
joliztoyco
I work in a refinery and every one of my crews has a dozen of these. A little different but the same function. I find a cord plugged in without one of these? It's not a good thing for the crew. But an even worse thing would be them not going home at night. I also instituted a quarterly inspection where i have 2 electricians inspect all their extension cords and test their GFI's....and we tag them with a different color for each quarter. ( A Union safety guy helped me write it up!)
spark-chaser1
The problem being that the average John Doe homeowner is NOT using a gfci in-line protector when using these to PERMANENTLY run power from an outside post light to their kids’ playhouse power, because they don’t know better.
We know the dangers, unfortunately… these are marketed to people who don’t and ultimately learn the hard way.
campanaelia
Ok, so let's imagine "the average John Doe homeowner" that purchased the 2 prong plug adapter and has a 3 prong cord cap he wants to plug in. His next move will be to use a 2 to 3 prong adapter. Even on a duplex receptacle, I've never seen the ground connected correctly to the center cover screw when using them. This just saves them the added inconvenience. Like you said, people don't now any better and will figure out a way to connect power regardless of safety.
mudshark61369
@campanaelia
" ... His next move will be to use a 2 to 3 prong adapter. Even on a duplex receptacle, I've never seen the ground connected correctly to the center cover screw when using them".
What good is connecting the ground tab to the outlet face plate screw on the 2 to 3 prong adapter if the circuit is an old two wire (hot/neutral) one meaning the box is not grounded? Joe Doakes home owner probably wouldn't think to check to see if the outlet or its box was grounded or not.
The problem is not the adapters themselves, it is the lack of visible warning on the packaging. Most have instructions about proper installation on the back of the hang card or box, in black and white. A red sticker saying read warning before use on the adapters would be helpful as would red inked WARNING: on the card/box.
Unfortunately, even that wouldn't always work, and the reason for that is in my signature.
campanaelia
I've retrofitted a few houses in my day to 3 prong receptacles and whether the boxes were grounded may vary. My first house built in 1951 had a separate ground wire bonding all the boxes. My parents house that was older 2 wire romex had no grounding, and even older hoses with knob and tube wiring, forget about it.
Probably the easiest way to check the wiring is with a receptacle tester...
varebelrose
"I've retrofitted a few houses in my day to 3 prong receptacles and whether the boxes were grounded may vary. My first house built in 1951 had a separate ground wire bonding all the boxes. My parents house that was older 2 wire romex had no grounding, and even older hoses with knob and tube wiring, forget about it."
The absolute best , safest, and most legal way to do this is to install GFCI protection either at the breaker or the very first outlet; everything downstream is protected and you are allowed to install 3 prong outlets even though there is no ground there (they do have to be marked "GFCI Protected"). Of course, AFCI's may also be required... it can be a can of worms to even touch old wiring, depending on the jurisdiction. Thats why it is always best to get a licensed person to do it.
campanaelia
I agree. Being a journeyman wireman, I did end up refeeding the houses with new romex and upgraded the services.
glenvonnie
Don't the neutral and the ground go to the same place, the ground ?, and if these outlets combine the ground and neutral inside, wouldn't that be safe ?
varebelrose
Yes, technically the grounded (neutral) and the grounding conductor go to the same place and should have continuity, but only at the point of origin. Everywhere else they are required to be kept separate. The ground(ing) conductor is there strictly for a safe return of voltage should anything not supposed to get energized... gets energized, not as a current carrying path. Even if this plug has them tied together (someone above said they are definitely not) it would still be an illegal and unsafe situation.
fab_finds4u
UL certification is needed if it plugs directly into an outlet.
mrmalibu
your completely right, but they still sell lamps and Xmas lights and a host of other products without a ground.
It's the laws that need to be changed to require a ground on all electrical plugs.
campanaelia
3 prong plugs are not required on many tools. electrical devices, and lighting. It is also cheaper for manufacturers. Xmas lights do not require ground since they are made of plastic and have a fuse in the plug for added protection. Lamps also don't require grounding as long as the wire is isolated from any metal parts. I doubt the NEC will change anything regarding this.
kathiec
You're not talking to eBay here. This is a member-to-member forum. And no matter how long your explanation or how many times you post it, eBay isn't going to stop selling this unless it's recalled or the government takes steps to ban it. So your efforts would be better spent trying to make one of those two things happen.
spark-chaser1
Another thing that will never happen, ( but something that I would love to see) is that people who use electricity ( outside of the profession) should have to take an educational course in electrical safety.
Electricity is like fire... Useful when harnessed and deadly when misused.
I see people doing stupid things with power all of the time. Until they or a loved one actually undergoes electric shock, arc flash/ burn or other exposure to the raw power of uncontrolled electricity, people will go on blissfully unaware of the sheer danger presented by misused electrical devices.
spark-chaser1
Chiming in as a licensed electrician... Stuff like this will always be sold, and people will always unknowingly use stuff like this and suffer property damage and/ or injury / electrocution/ death.
I see it all of the time. Quite often after the fire department has put out the smouldering cinders of what used to be a family's house, or after someone standing in ankle deep floodwater tried to plug in a sump pump.
If nothing else, thank you for making people aware of stuff like this. I get frustrated seeing stuff of this sort, just knowing what will happen when people use garbage like that. I can see this being used in a non- gfci protected outside light fixture in the rain to power Christmas lights and whatnot while kids are hanging off of them.
Yes... Stuff like this will always be sold. Unfortunately.
edwgre_87
OPGuide
Any ideas on how to get through to eBay, or even the supplier who sells this dangerous adaptor to many of the sellers on eBay.
I have a list of at least 70 sellers, some who have discontinued selling it after I have warned them of the dangers.
How do I get through to and contact the supplier who actually sells it to the sellers. Maybe they will care especially when they know how liable they are if someone gets hurt?
spark-chaser1
Sorry... We cross- posted. I hate to say it, but nobody will listen. You will have to virtually go from seller to seller and appeal to them to stop selling such non- listed junk.
If the NFPA hasn't shut this stuff down, I don't see eBay doing it.
As an electrical professional, I spread the word where I can, when I can, and that's the most that can probably done. We won't be able to save the whole world from itself, but we can tackle things locally and hope for the best.
kathiec
Unless the plug is the subject of a recall or illegal to sell in the US you can't stop eBay from listing it. Thinking you can is just going to be a never-ending round of frustration.
edwgre_87
OPYes, it is frustrating, especially since eBay does not seem to care at all!
They are the ones that allow this dangerous adaptor to be sold!
edwgre_87
OPSo how do I contact eBay in hopes of getting them to take this seriously?
So far it seems like they just do not care about the dangers involved!
THIS e26 PLUG ADAPTOR IS NOT SAFE TO USE!
WHEN THE GROUND CONNECTION IS NEEDED!
buyselljack2016
Good luck with that.
Such adapters as that have been around (I have used such)for at least 40 years that I know of. Likely longer than that.
You need to start at a higher level. Get the federal government to stop the sale of any such deice.
You will also need to stop the importing of such.
edwgre_87
OPRockstar
Yes 2 wire e26 plug adaptors have been around for a long time and safe if designed properly.
This new 3 wire adaptor is the DANGEROUS ONE. It has an open ground, which is NOT SAFE AT ALL!
-----------some more info as to why--------
This plug adapter seems to work fine, so
WHY IS THIS PLUG ADAPTER DANGEROUS?
It has an open ground not connected to anything. (a very unsafe design)
WHY IS AN OPEN GROUND DANGEROUS?
Think of the “Safety Air Bag†which is in your car.
It does nothing until an accident occurs, then it is very important for your safety. Yes, very important that it opens quickly.
The same is true with a ground connection in an electrical circuit.
It does nothing until an accident occurs, and then the ground connection is important for your safety.
(this fact is misunderstood by most people, so they think the device is safe because it works fine during NORMAL use!)
What would happen if your car safety air bag was never connected.
When an accident occurred, you would be seriously injured and very upset as to why the air bag was not connected.
What would happen if the ground in your electrical circuit was never connected?
When an accident occurred, you would possibly be injured, and very upset as to why the ground was never connected and left open.
You could possibly get an electrical shock, fall off a ladder, etc., or even death by electrocution.
But again, the ground is only important when an electrical malfunction, problem or accident occurs.
That's why many people think that this adapter works fine since no electrical malfunction has occurred.
But when that electrical problem or malfunction does occur, that's when you will need a good reliable ground connection.
This plug adapter once again, has an OPEN GROUND connection, which is VERY DANGEROUS.
PLEASE STOP SELLING THIS DANGEROUS PLUG ADAPTOR
And notify your supplier to the same dangers!
The manufacturer needs to stop making and selling this DANGEROUS ADAPTOR.
YOUR HELP IS NEEDED TO ENSURE THE SAFETY OF YOUR CUSTOMERS!
varebelrose
"It has an open ground"
No debate that these are dangerous for an ignorant user, but I would strongly suspect that the 3rd prong ground is not open, but bootlegged onto the neutral connection.
As far as UL or CSA listings, it is up to the consumer to make informed choices about the items they purchase and use. We cannot protect everyone from everything.
Also a licensed electrician since 1986.
spark-chaser1
35 years here. I’m sure you’ve also seen your share of interesting residential wiring modifications and have seen things such as I have. My comments stem from many interesting troubleshoots where issues are traced back to stuff like this being used.
many of the types the OP is talking about are definitely not grounded, nor piggybacked off of the screw shell neutral. That third port is open on a lot of those.
hopefully the OP gets somewhere with this, because I know I won’t.
this is why I enjoy now working Industrial jobs…. Qualified personnel only. ðŸ‘ðŸ»
varebelrose
"this is why I enjoy now working Industrial jobs…. Qualified personnel only."

I couldn't agree more! My workplace since 1990...
spark-chaser1
You guys hiring?ðŸ‘ðŸ»
edwgre_87
OPRock star
I also thought that was a possibility (gnd to neutral), but I purchased 3 of them from different sellers and they all have open grounds! Just a very dangerous and misleading design.
Looks like you have a ground, when actually you DO NOT!